boards start at the bottom, nearest mainswitch on the left row, up to top and then the bottom of the right row upwards.
if you have one side full of breakers and then the next side has one in it and rest are blanked ive always seen it as bad practice and it looks kack.
so from bottom left, MCB1 cables go to bottom left terminal 1 for earth and neutral
from mcb 2 n+e to terminal 2
if its three phase then stabs 1, 2 and 3 are occupied by the mcb so N+E of circuit go to terminal 1 on the earth bar
then next 3ph mcb occuipes 4,5 and 6 so n+e go to terminal 4
it has nothing to do with "being easy to check because its wired in twin" YOU SHOULD NOT HAVE TO CHECK IF DONE PROPERLY (obviously, you never know somone elses work so should check but if you have a few 1000 cables matching em when incorrectly wired wont be fun)
all cables should be installed uniformly, and when adding to a board you should follow atleast the wiring scheme, as you can see, me and jim work to one variation, he uses second terminal for 3 phase breakers, i use first terminal, to anyone knowing their job it will takeall of 10 seconds to work out.
i can see what your getting at though, and if i remember correctly the bottom terminals of the e+n bars are occupied by the incoming earth setup and bonding, on N the N link occupied the very top terminal.
check out P10200ee.JPG on the same site, should be a little clearer